Semantics of "Area Classification" and who should determined Areas
MrJLH
CO
Curious on opinions of of what area classification drawings should be called for a petrochemical facility :
Hazardous Area Classification Drawings
or
Electrical Area Classification Drawings
or other titles.
Curious on other opinions on who should determine the extent of the hazardous area(s).
Electrical Engineer
or
Area Process Engineer
Thanks
I don't think there is a specific name for a document that describes the extent of a classified area. I have seen some drawings that are fairly detailed that lay out where there are classified areas in a building. I've also seen a text document that was no more than a few paragraphs that described what areas were classified.
As for who should do the classification it should be someone who is qualified to do so.
I agree with that answer, but I have experienced confusion with this issue several times in my career. In my opinion, it is ultimately the Architect's responsibility to have it accurately reflected on the plans. Like emergency egress lighting. For which they would bear the responsibility to seek out a person who is intimately knowledgeable in the subject. That, of course, is often, not what happens.
Not the E.E.
Not the E.E.
or
or other titles.
Electrical Engineer
or
Thanks
As for the naming I would not call them Electrical Area prints because they also reflect on other things such as, non sparking tools, lift trucks, smoking, open flames.....
The same reason goes for who does the classifications, it is not just electrical.
Cowboy
Ultimately it would be Engineers selecting the area classifications, but unless you are working on new engineered construction it likely won't be the case. In my situation since I was a field service man to today where I'm drawing plans for our products, I'm the one making the selections. I think it's important if we are in the industry to learn to do so with a reasonable level of confidence and accuracy. I don't claim to be perfect, but I think I get it right most of the time.
Ultimately it is the owner's responsibility. He can chose to pay the architect to take on that task, but it is the owner's responsibility.
I don't know quite how "I'm drawing plans for our products" or "I'm the one making the selection" is meaningful in context of the question the OP posed. Neither comment would seem to have anything to do with determining whether an area should be classified or not, and if so what it should be classified as.
In a way, everything is the owner's ultimate responsibility, however,for many things law requires professionals to perform tasks. I think at issue here is the responsibility to do the classifying. It is odd that there doesn't seem to be a clear responsibility of a specific engineering or architectural license this task is assigned to.
why should there be? as long as it gets done why does there need to be a law about it?
in any case, it seems to vary a lot as to just who performs this task. often the insurance company is the one who determines such things, or at least decides who is acceptable to determine them.
Perhaps law is not the right term. I mean it should be spelled out in the State building code. And the why, is because it is one thing I have seen poorly done over and over, and also have had major trouble getting properly done when necessary. To me, it equates to say, fire alarm design. It is clear in my State who can and can't design a fire alarm system.
fire alarm systems are often poorly designed. just having a license does not mean it will be done right any more than having an electrician license means electrical work will be done any better. we want to think it works that way, but there are a lot of licensed hacks in a lot of fields.
look at the medical field. just about any employee in the same building as a patient is licensed yet medical malpractice is the number one cause of preventable deaths.
in any case, the state building code generally has the force of law.
Agreed, but if the code designated who was responsible it would make my job easier, even if it just meant you had a person to point the finger at, while correcting their mistakes, like fire alarm.
Presumably the contract designates this. Why not look there instead of trying to pass another unneeded goofy law?
I’ve been following this thread with some interest. I’m going to cite a few excerpts of the NEC and other Standards. I've added a few underlines for emphasis and ellipsis (…) for omitted but irrelevant material.
From the NEC:
ARTICLE 500
Hazardous (Classified) Locations,
Classes I, II, and III, Divisions 1 and 2
InformationalNote: Rules that are followed by a reference in brackets
containtext that has been extracted from NFPA 497-2012,
Recommended Practice for the Classification ofFlammable
Liquids, Gases, or Vapors and of Hazardous(Classified)
Locations for Electrical Installations in ChemicalProcess
Areas, and NFPA 499-2014, Recommended Practice for the
Classification of Combustible Dusts and ofHazardous
(Classified) Locations for Electrical Installationin Chemical
Process Areas. Only editorial changes were made to the
extractedtext to make it consistent with this Code.
500.1 Scope - Articles 500 Through 504. Articles 500
through 504 cover the requirements for electrical and electronic
equipmentand wiring
for all voltages in Class I,
Divisions I and 2; Class II, Divisions 1 and 2;
and Class III, Divisions 1 and 2 locations where fire or explosion
hazards may exist due to flammable gases, flammable
liquid-produced vapors, combustible liquid-produced vapors,
combustible dusts, or ignitible fibers/flyings.
500.4 General.
(A) Documentation. All areas designated as hazardous
(classified)locations shall be properly documented. This
documentation shall be available to those authorized to design,
install, inspect maintain, or operate electrical equipment
at the location.
(B) Reference Standards. Important information relating
to topics covered in Chapter 5 may be found in other publications.
Informational Note No. 1: It is important that the authority
having jurisdiction be familiar with recorded industrial experience
as well as with the standards of the National Fire
Protection Association (NFPA), the American Petroleum
Institute (API), and the International Society of Automation
(ISA), that may be of use in the classification of various
locations, the determination of adequate ventilation, and the
protection against static electricity and lightning hazards.
RBALEX NOTE: Depending on the NEC Edition there are five or six FPN/INs. All are important; FPN/IN No.2 particularly for this discussion since it deals with many specific external reference Standards. Again in particular NFPA 497 (listed in the Article 500 IN/FPN) and API RP 500 are among the external Standards listed in FPN/IN No.2
From NFPA 497:
NFPA 497
Classification of Flammable Liquids, Gases,
or Vapors and of Hazardous (Classified)
in Chemical Process Areas
Chapter 1 Administration
1.1 Scope.
1.1.1 This recommended practice applies to those locations
where flammable gases or vapors, flammable liquids, or combustible
liquids are processed or handled; and where their
release into the atmosphere could result in their ignition by
electrical systems or equipment.
1.1.2 This recommended practice provides information on
specific flammable gases and vapors, flammable liquids, and
, whose relevant combustion properties
have been sufficiently identified to allow their classification
into the groups established by NFPA 70, National Electrical
Code® (NEC®), for proper selection of electrical equipment in
hazardous(classified) locations. The tables of selected combustible
materials contained in this document are not intended
to be all-inclusive.
From API RP 500
Recommended Practice for Classification of Locations for Electrical Installations atPetroleum Facilities Classified as Class I, Division 1 and Division 2
1 Scope
1.1 Purpose
1.1.1 The purpose of this recommended practice is to provide guidelines for classifying locations Class I, Division 1 and Class I, Division 2 at petroleum facilities for the selection and installation of electrical equipment. Basic definitions given in the 2008 Edition of NFPA 70, National Electrical Code (NEC), have been followed in developing this recommended practice. This publication is only a guide and requires the application of sound engineering judgment.
1.1.2 Electrical installations in areas where flammable liquids, flammable gases or vapors, or combustible liquids are produced, processed, stored or otherwise handled can be suitably designed if the locations of potential sources of release and accumulation are clearly defined. Once a location has been classified, requirements for electrical equipment and associated wiring should be determined from applicable publications. Applicable publications may include NFPA 70 and API 14F. Reference Section 2 for publications for other possible applications.
1.2 Scope
1.2.1 This document applies to the classification of locations for both temporarily and permanently installed electrical equipment. It is intended to be applied where there may be a risk of ignition due to the presence of flammable gases, flammable liquid-produced vapors, or combustible liquid-produced vapors, mixed with air ,under
normal atmospheric conditions (identified throughout this document as “gases and vapors”). Normal atmospheric conditions are defined as conditions that vary above and below reference levels of 101.3 kPa (14.7 psia) and 200 °C (68 °F)provided that the variations have a negligible effect on the explosion properties of the flammable materials.
I basically endorse petersonra’s initial answer: Call the required [Section 500.4(A)] documentation what you want and have a qualified individual do it.
Some personal observations:
Note NFPA 497 and API RP500 clearly state their purpose is for selecting electrical installations. If you use the documentation for anything else, that’s fine, but, if I created it and you want to use it for road ways, smoking areas, fire proofing structures, etc., don’t ask me to modify it – I create electrical area classification documentation.
My kind of issue is why should the electrical engineer bear the responsibility and hold the liability of determining the hazardous area class of a facility. Is it not the process engineers who have the most familiarity with the process equipment and process conditions.
I feel like when I see area class drawings that were/are done by our EPC's all that was done was copy and paste the application of the API figures without any actual true understanding of the process and what the actual literature of API says in determineing the extent of the areas.
I don't think the title of the person(s) making the determination matters much. What matters is if he/she/they are competent to do so.
If you believe an area classification is in error you certainly should bring your concerns to the attention of someone who is in a position to do something about it.
Part of the original discussion was who should be responsible for area classifications, I was expanding on the topic as it applies to me, and I think needs to apply to many of us who work in the industry. I didn't however, ever imagine I would need to defend my comments.
This is the nub of the discussion. How would I, or anyone for that matter, prove competence? I have 11 years of experience dealing with chemical processes around nitroglycerin. Does that make me qualified? To answer honestly, I'd have to say "not necessarily". There are tons of training courses on NFPA 70E. I don't think I've ever seen one on 497, RP 500, or focusing on Article 500. Other than design, rinse, repeat, how can a designer maintain proficiency?