The term "Vector Motor" is just a marketing term used by Baldor. It is just an Inverter Duty motor with a wide speed range (see below) and an integral independent blower attached to it, along with standard options for Encoders.
An "Inverter Duty" (not a true design specification by anybody either) motor is typically referring to a motor designed to be operated at less than full speed and with features necessary to have it survive in the sometimes electrically nasty environments that come with being connected to an inverter. So from that standpoint, if you have a motor that says it is "Inverter Duty", it may be fine. But as I mentioned, there is no universally accepted third-party specification as to what "Inverter Duty" means, so it is sort of up to you to look carefully at your application and the motor specs to make sure it will survive. Vector or non-vector makes no difference in the motor really. BUT...
There are going to be differences from one Inverter Duty motor to another, usually based on the Speed Ratio (or Range) it is rated for. If for instance your motor says it is rated for a 1000:1 Speed Ratio, that means if it is an 1800 RPM motor it can be run at 18 RPM without external cooling. If it says 2000:1, it can go down to 9 RPM. If it says 100:1, it is only good down to 180 RPM though and if it doesn't say anything, I wouldn't trust it. But it should, even if it isn't on the nameplate. You may need to go back to the mfr for specs.
So... because of the fact that people usually use Vector Drives for low speed applications, you could make an assumption that a motor with a 2000:1 speed ratio could be considered better for Vector operation than one rated at 100:1. But if you are operating at 30% speed or higher, it would make little difference; in other words the 100:1 motor would be fine for vector operation.
Back to your application; if you are NOT currently using the Vector mode in the VFD at those speeds, it would be likely that your motor will stall and overload. In V/Hz mode, the best you can typically hope for is a 4:1 speed ratio. So for an 1800 RPM motor, that is down to 250 RPM. When you get slower than that, the motor output torque is unstable and may or may not allow for acceleration without overloading. But if your motor, Inverter Duty or not, is not rated for a high speed ratio, running it at low speeds will not be possible or may require external cooling.