inspector 102
Senior Member
- Location
- Northern Indiana
Main Structure has 200 amp single phase panel with CCE. There will be a 100 Load side panel located in the structure fed by 4-4-4-4 cu feeders. Then there will be a feeder extended to a detached building with a 60 amp load side panel. My understanding is this would also be fed with 4-4-4-4 cable but then also grounded to an approved grounding system via 2-ground rods per 250.53(g) and 250.56. The middle load side panel will have no additional grounding means other than the grounding conductor pulled as the feeder assembly. Am I correct on the application of this since there is a panel between the MDP and the last load side panel. Going to the detached structure has me a little confused. Thanks for help.
Note: I think the minimum size of grounding conductor would be #8 cu for feeders per Tab 250.66, but they have proposed #4.