hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Attached sketch show building with parking, first to fourth floor. The grade is sloped. The building is Not a high rise.
Parking is construction II and first floor to fourth floor is construction III therefore they are both separated by Firewall. Building code department has labeled the parking part and first to fourth floor separate buildings. AHJ here has local amendment that definition of building in the NEC follow Building code department thus we are to treat parking space and first to fourth floors two separate buildings horizontally.
There are two vertical parts: part I and part II buildings but vertically it is Not considered separate buildings as far as I know so we can assume they are Not separate buildings vertically.
The main service switchboard is located on part II first floor and generator, fire pump on part I parking level
From switchboard their is service conductor tapped ahead of service disco in switchboard going to underground part II then come up fire pump main service disco in parking part I.
Also from switchboard I have feeder conductors going underground then come up part I parking and feeding generator ATS-S, ATS-E normal side fused discos standby and emergency
The switchboard also has feeder conductors going underground to come up in part I parking then pass thru and feed Panel LGW 1st floor Part 1, meter stacks MLO part 1 as shown in sketch.
The panel LGW part 1 1st floor has branch circuits which feed the parking which by building department is separate building but they all feed inside buildings don’t go outside.
Questions:
1. The switchboard feeders that go underground from part 2 first floor to part 1 parking are they considered outside feeders NEC 2017 section 225 or not? Your opinion
2. The switchboard feeders that go underground from part 2 first floor to part 1 parking which feed normal side of emergency and standby ATS would they be allowed by NEC 2017 section 225 or not?
3. The switchboard feeder that go underground from part 2 first floor come up part 1 parking and then go to part 1 first floor which then feed Panel LGW should it have disco and grounding electrode system right where they enter part 1 parking or not NEC 2017 sections 225, 250.30?
Sketch:
Parking is construction II and first floor to fourth floor is construction III therefore they are both separated by Firewall. Building code department has labeled the parking part and first to fourth floor separate buildings. AHJ here has local amendment that definition of building in the NEC follow Building code department thus we are to treat parking space and first to fourth floors two separate buildings horizontally.
There are two vertical parts: part I and part II buildings but vertically it is Not considered separate buildings as far as I know so we can assume they are Not separate buildings vertically.
The main service switchboard is located on part II first floor and generator, fire pump on part I parking level
From switchboard their is service conductor tapped ahead of service disco in switchboard going to underground part II then come up fire pump main service disco in parking part I.
Also from switchboard I have feeder conductors going underground then come up part I parking and feeding generator ATS-S, ATS-E normal side fused discos standby and emergency
The switchboard also has feeder conductors going underground to come up in part I parking then pass thru and feed Panel LGW 1st floor Part 1, meter stacks MLO part 1 as shown in sketch.
The panel LGW part 1 1st floor has branch circuits which feed the parking which by building department is separate building but they all feed inside buildings don’t go outside.
Questions:
1. The switchboard feeders that go underground from part 2 first floor to part 1 parking are they considered outside feeders NEC 2017 section 225 or not? Your opinion
2. The switchboard feeders that go underground from part 2 first floor to part 1 parking which feed normal side of emergency and standby ATS would they be allowed by NEC 2017 section 225 or not?
3. The switchboard feeder that go underground from part 2 first floor come up part 1 parking and then go to part 1 first floor which then feed Panel LGW should it have disco and grounding electrode system right where they enter part 1 parking or not NEC 2017 sections 225, 250.30?
Sketch: