Hello,
I have a situation where I have 2 buildings.
Building 1:
Has the Service Entrance (480/277V, ~400A)
Has a Standby Generator
Has a 3 pole ATS with a solid neutral.Takes in the POCO and the Standby Gen feed.
The 3 Pole ATS feeds a Double Throw Safety Switch (DTSS), the DTSS also takes in a feed from a Roll up generator tap box.
The DTSS feeds a Distribution panel which in turn feeds Building 2.
Building 2:
Gets a feed from building 1 and the feed is received into a DTSS.
the DTSS second source is from a roll up generator.
Under normal every days conditions, the utility is feeding building 1 and building 2. In the case of loss of power, the ATS switches to the Standby generator. In the case that the standby generator fails, the client can roll up a generator at building 1 to feed building 1 and building 2. However, if the client cannot acquire a generator large enough to feed both building 1 and building 2, the client has the option to feed building 2 from its own roll up generator.
See attached quick sketch for an overview of the above. View attachment Multiple Gens Switched Neutral.pdf
Question:
Does the Double Throw Safety Switch at building 2 need to have a switched neutral? My concern is during the situation of building 1 utilizing roll up gen and building 2 utilizing roll up gen.Even if all of the generators are properly not having their neutrals bonded to ground, in the case of a fault at building 2, the fault path back to the generator at building 2, would need to go through the neutral - ground connection located all the way back at the service entrance. The neutral in that area would already be loaded with the loads of building 1 and I am worried that it could be overloaded.
Building 1:
Building 2:
Question: