I've seen on this forum multiple times that if you are using 90C rated wire at its 90C amperage rating (e.g. #12 THHN for 30A), and you want to upsize the conductor in order to terminate it in 75C terminals (in this case, from #12 to #10), you need to make those splices using 90C connectors "in a separate, otherwise empty enclosure".
I assume the reason it has to be a separate enclosure is because you can't have the temperature exceeding the terminal's rating anywhere within the terminal's enclosure, in order to not overheat the terminal itself. Therefore you need to keep the conductor that may possibly reach 90C out of an enclosure with 75C terminals.
I do not understand why the separate enclosure has to be "otherwise empty". I also couldn't find this anywhere in the NEC, although I will admit that my code proficiency is work in progress...
The only thing I could think of is that "otherwise empty" just means "empty of anything with a lower temperature rating", rather than "empty of other splices and conductors passing through". Is this the correct answer or is there something else going on that I'm missing?
I've seen on this forum multiple times that if you are using 90C rated wire at its 90C amperage rating (e.g. #12 THHN for 30A), and you want to upsize the conductor in order to terminate it in 75C terminals (in this case, from #12 to #10), you need to make those splices using 90C connectors "in a separate, otherwise empty enclosure".
I assume the reason it has to be a separate enclosure is because you can't have the temperature exceeding the terminal's rating anywhere within the terminal's enclosure, in order to not overheat the terminal itself. Therefore you need to keep the conductor that may possibly reach 90C out of an enclosure with 75C terminals.
I do not understand why the separate enclosure has to be "otherwise empty". I also couldn't find this anywhere in the NEC, although I will admit that my code proficiency is work in progress...
The only thing I could think of is that "otherwise empty" just means "empty of anything with a lower temperature rating", rather than "empty of other splices and conductors passing through". Is this the correct answer or is there something else going on that I'm missing?