Separate structure with existing 3 wire 240v service

Status
Not open for further replies.

yetiman

Member
Customer with existing UF 3 wire 240v feeder to well house only serving 240 volt loads( well pump and small heater). They need a 120v circuit for a water softener. I am thinking I can add a new panel with service disconnect, add electrodes, re bond that bare equipment ground and use that as a grounded conductor for the 120v loads. Code allows a 3 wire feeder if no metallic path back to the source ( 250.32 B2) which this has a plastic pipe between structures. I don't see a specific requirement for an insulated grounded conductor in this case. What say you all?
 
Current code allows this for existing installations so I would imagine your inspector would allow it.

Since you are only running one piece of equipment the EGC is probably sized big enough to be a grounded conductor.
 
Well, gee wilickers Wally, I done knowed that.

What the Beaver wants to know is "Code reference, please." Then he will shut up.:)

Well I gave it a hard look and couldn't find anything that said outright that a grounded conductor had to be insulated, but the only place I could find express permission for it to be uninsulated was for services in 230.22 and 230.30. I'm going to have to spend some time in the dandelion patch and sort this out.
 
Well I gave it a hard look and couldn't find anything that said outright that a grounded conductor had to be insulated, but the only place I could find express permission for it to be uninsulated was for services in 230.22 and 230.30. I'm going to have to spend some time in the dandelion patch and sort this out.

I am with you, when I posted "200.something" I was on the road. When I had a chance I went looking and so far I found the same as you.

I can't even find a general requirement for hot conductors to be insulated. :huh:
 
Find a 240 volt water softener.
Or set a 240x240/120 xfmr and establish a ground for the neutral

Yes, I know I can do that. That is called stating the obvious. I was looking for the code requirement that says it cannot be un insulated, not because the inspector says so.
 
I hadn't thought of using a step-down transformer to eliminate the need for the neutral wire from the main panel to the sub panel. I'll have to remember this.

Of course on new installations, I'm going to pull both an equipment grounding conductor and a neutral wire, along with the electrical conductors.

However my State Electrical Inspector is also going to require the following:

1. a 125 V single phase recepticle outlet, 210.50G2 or 210.64
2. Interior and exterior lighting outlets 210.70
3. Metallic well casing grounded 250.52A8

I WILL get a correction notice if I don't do all the above.
 