Here is what UL states that this remote panel has to conform with. Notice the bold type. Also notice the requirement to label the service disconnect in line 24. This is the 2004 Guide so the NEC references will fall under the 2002 cycle. For a complete reading
http://www.ul.com/regulators/panelboards.pdf
SUITABLE FOR USE AS SERVICE EQUIPMENT
18. These are the basic requirements that a panelboard rated 600 volts or less must meet in order to be used as service equipment:
A. Service disconnecting means must be provided.
B. Each service disconnect provided must have a switching feature that disconnects all conductors from the service-entrance conductors and that is suitable for use as a service disconnect. There is one exception: the neutral service conductor can be disconnected by removing the wires from the pressure wire connectors on the service neutral bus as noted in Section 230.75 (230?75) of the NEC.
In general, snap, toggle or similar switches, are not acceptable because their internal electrical spacing are too small. The exception in Section 225.36 (230?84(b)) of the NEC for branch circuit switches used to disconnect garages and out buildings on residential property does not apply to the service disconnects in a panelboard.
Circuit breakers, either molded case, fused, or in combination with ground fault circuit interrupters, are suitable for use as service disconnects. Other devices that are used to protect individual circuits, circuits within equipment or appliances, or circuit protectors without on and off features, are not suitable for use as service disconnects.
22. Some panelboards may have the required number of handles and service overcurrent devices, when the maximum number of the smallest units are installed and used without handles or ties or similar devices. These panelboards may have the shorter marking ?Suitable for use as service equipment? or ?Suitable only for use as service equipment.? The shorter marking is suitable for Class CTL (circuit limited) lighting and appliance panelboards since they cannot have more than two main overcurrent protective devices as specified in Section 408.16(A) (384-16(a)) of the NEC.
23. Class CTL lighting and appliance panelboards without main overcurrent protection usually are not marked suitable for service equipment use. Such panelboards, with not more than 10 percent of theircovercurrent devices rated 30 amperes or less, however, may be suitable for use as service equipment. They are marked ?Suitable for use as service equipment when not more than six main disconnecting means are provided and when not used as a lighting and appliance branch-circuit panelboard; see Section 408.14 (384?14) of the NEC.?
24. A panelboard intended for service equipment use must have the marking ?Service Disconnects? near the switch or circuit breaker handles. If this is not done in the factory, pressure sensitive labels must be provided. This marking identifies the service disconnects when branch disconnects are also present. This is required by Section 230.70(B) (230?70) of the NEC.
For what ever reason that I cannot understand there is a misconception that a panel at a remote building with six or less single pole breakers that protect branch circuits will fulfill the requirements of 225.33(B). This is not true no more that the assumption that six or less single pole breakers will fulfill the requirements of 230.71(B). Both of these sections have the same wording which states that handle ties shall be permitted on multiwire circuits. It does not say that handle ties can be used on multiple circuits.
In the UL Marking Guide it clearly states that in order to be listed as ?Suitable for use as service equipment? while being used as a lighting and appliance panelboard not more than two mains is required.