I have separately derived generator system. The generator has to two main breakers 1600AT and 400AT. The 1600AT has feeder 4 sets of 600kcmil and the 400AT breaker has feeder 1 set of 600kcmil.
Engineer has provided #2/0 awg grounding electrode conductor. I am not sure how to size grounding electrode conductor should it be sized based in sum of feeders 1600AT and 400AT, summing parallel sets or the largest one of the two breaker feeders. What should the grounding electrode conductor size be #2/0 awg or 3/0wag? How to size it?
Engineer has provided #2/0 awg grounding electrode conductor. I am not sure how to size grounding electrode conductor should it be sized based in sum of feeders 1600AT and 400AT, summing parallel sets or the largest one of the two breaker feeders. What should the grounding electrode conductor size be #2/0 awg or 3/0wag? How to size it?