the GES impedance to earth is uncontrolled. And if a secondary conductor faults to anything else, the presence of a low impedance fault path does not depend on the presence of the secondary GEC.
I don't know if I agree with that. While it shouldn't be used as the fault path, it can be part of the path. And as the resistance grows, so too would the voltage seen across that resistance. Since the fault current would be "constant". Though with a proper EGC that current would be minimal or none.
From the Green Book, IEEE 142, chapter 4.1.3, "The development of a low-resistance ground electrode is of paramount importance to satisfy the requirements for system feeders from utilities, where the fault return path is via the ground. Also, secondarily, as a backup to the equipment grounds, which may occasionally be open-circuited unintentionally. Logically, the lower the resistance of the grounding system, the more adequately these requirements are met."
Their point is that the GES/GEC being of low resistance does serve a purpose. Their noted reasons do not include being the desired ground fault return path, nonetheless, it is one. Their main reasons were as Electron Sam said.
There are other mentions in chapter 1 about the required resistances needed to ensure it is effectively grounded but I don't think those would apply. The resistance of the EGC would probably still satisfy those. Unless a really small primary breaker was used for a large transformer but then you wouldn't be able to use it due to inrush. So, that would kinda defeat that premise.
So why is a GEC not subject to this impedance? And where is all this fault current flowing on the GEC coming from? The only time I see any fault current flowing on a grounding electrode conductor is from contact with medium voltage lines. That is extremely rare, and besides we were originally talking about a separately derived system which is unlikely to have contact with higher voltage lines.
It is.
But the NEC does not cover the calculations of ground resistance. They only specify that an additional electrode can be required if more than 25 ohms. Frankly, nobody does those calculations for circuits of less than 1000V any more. I think they used to in Canada. It would be abnormal to have fault current through earth but it can / does happen. It would not be nearly as much as a utility but it is still relevant since the NEC covers more than just dry types for an office. There are numerous industrial locations that would have their own MV separately derived systems that utilize a ground grid or similar ground studies just for this purpose.
The Soares Grounding and Bonding book goes into more detail about the grounding electrode conductor ampacity, long runs of emt used as a EGC, etc. Things that aren't addressed by the NEC but could be relevant.
Again there is not fault current flowing on the gec, that is not its purpose. Also I was not talking about ungrounded systems.
While it is not supposed to, there can be current flow through connected electrodes or bonded metal piping if they are a parallel path back. Similar to how a EGC and the metal conduit can act as parallel paths back.