Greetings. Long time reader, new poster. Sadly, this is on the topic of grounding and bonding of a separately derived system, this time a generator and transformer.. I have a tricky situation with the voltage on a panel fed by a transformer at a commercial location. The panel in question is fed through an ATS to its "main panel." A 3 phase breaker feeds 480 volts to a transformer which feeds 120/208 volts to the trouble panel. The trouble is that the transformer, nor the sub panel are bonded neutral to ground. Of course, this is giving me wild voltage readings of neutral to ground and ground to hot. I very briefly attempted bonding the neutral to ground at the transformer and it did not like it (sparks, immediate signs of over current). The feed "main panel," fed through the ATS is bonded and voltage readings are fine at that point, but everything goes astray at the transformer." There is another, identical transformer in the same room feeding a different panel. but not connected to a generator and the transformer is bonded, thus the voltage readings at the panel are fine. Everything seems to be solidly grounded, but the neutral is floating.
My questions:
In what situation should the transformer, nor the secondary panel not be bonded?
If it is a case of being run through a generator, then why would the primary panel be bonded?
I don't think I am an idiot, but am I being an idiot??
Much appreciated.
My questions:
In what situation should the transformer, nor the secondary panel not be bonded?
If it is a case of being run through a generator, then why would the primary panel be bonded?
I don't think I am an idiot, but am I being an idiot??
Much appreciated.