So what are we left with when the SDS is located outside as far as bonding
Treat the supply just like you would a utility supply, bond the neutral at the outside source run a duel purpose natural / bond to the building and bond that conductor at the building
Bond the neutral at the outside source run what looks like a traditional feeder into the building and only bond the “ equipment ground” to the building grounding system.
Keep in mind the bonding conductor what your referring to as an equipment ground is actually the bond from the SDS system neutral to the buildings equipment grounding system / which also is bonded to the building grounding electrode system
Treat the supply just like you would a utility supply, bond the neutral at the outside source run a duel purpose natural / bond to the building and bond that conductor at the building
Bond the neutral at the outside source run what looks like a traditional feeder into the building and only bond the “ equipment ground” to the building grounding system.
Keep in mind the bonding conductor what your referring to as an equipment ground is actually the bond from the SDS system neutral to the buildings equipment grounding system / which also is bonded to the building grounding electrode system