VanmBuilders
Member
- Location
- California
- Occupation
- Contractor
Hello, have a main utility service cabinet That has 600 amp breaker feeding two 200amp breakers and one 125amp breaker inside the same cabinet. 125 amp breaker feeds directly to a primary 75 kva 480volt delta/secondary 208 volt y transformer. A neutral wire was ran with the three hot legs inside conduit from125amp breaker but neutral wasn’t attached to XO lug. The neutral is terminated by means of a knuckle. There is also no green wire in that conduit raceway coming from the 125amp breaker. At one time this 125amp raceway was attached to a panel near a utility room. However now diverted to a transformer. So I’m assuming this is a separately derived system. And transformer creates a new system bond via XO with its own ground rod and neutral bond for 208 service cabinet with a separate ground and separate neutral at the new 208v panel.
Last edited: