Ragin Cajun
- Upstate S.C.
But the table for conductors #2 or smaller lists #8. The primary conductors are #4. Table 250.102(c)(1) OR 250.66. what did I miss?Ah, but it's not large enough.
The secondary conductors and ampacity.But the table for conductors #2 or smaller lists #8. The primary conductors are #4. Table 250.102(c)(1) OR 250.66. what did I miss?
It seems to me the diagram shows a bonding jumper between N and G at two places. Is this allowed?Note, all I have to go on is the photo they sent me.
All the green wires are interconnected
One originates at the 3000A 480V switch gear feeding the transformer.
The other go to the new 120/208V panelboard.
Apparently since they could not find any building steel, etc. the grounding electrode conductor, conduit, etc. were not run shown in the detail below. I don't know what more that can be done.
Good catch. One location only. SDS or the panel.It seems to me the diagram shows a bonding jumper between N and G at two places. Is this allowed?
You size the GEC and SSBJ based on the secondary conductor size or in this case 1/0.But the table for conductors #2 or smaller lists #8. The primary conductors are #4. Table 250.102(c)(1) OR 250.66. what did I miss?
Based onm your 1/0 secondary it would need to be a #6I do have the #8 in the 1"C I can use for the GEC.