I?ve noticed that the long-running controversy regarding the definition of an SDS has surfaced again in another thread. Statements were made about not ?confusing the new people in the trade?.
As an educator, this is also one of my concerns, and I offer the following in the interest of trying to resolve the controversy.
The term "separately derived system" is just a name used to identify a premise wiring system supplied from a source other than the main service transformer. When the use of step-down transformers and stand-by generators became common, a name was needed to identify the wiring systems that they supplied.
As some others have stated, the wording of the definition may not be perfect, but I think the intent is clear. The key is the interpretation of the words "electrical connection".
Referring to the sketch below, the 480/277 volt service (System 2) ends at the dry-type transformer. The 208/120 volt system is separately derived (System 3) and both are required to be grounded.
They are completely separate systems in terms of any current flow from one to the other, because they are connected to each other at a single point, the ground bus (A) in the dry-type transformer. There is a "connection" but not one over which current can flow.
Any load and/or fault current originating from either transformer is confined to that system, and can only flow back to it?s point of origin. Live-to-enclosure faults (aka ground faults) in both systems are illustrated.
Other than the problem of clarifying the definition of an SDS, there is no technical or safety issue.
Comments are welcome.
Ed
[ January 08, 2004, 10:13 AM: Message edited by: Ed MacLaren ]
As an educator, this is also one of my concerns, and I offer the following in the interest of trying to resolve the controversy.
The term "separately derived system" is just a name used to identify a premise wiring system supplied from a source other than the main service transformer. When the use of step-down transformers and stand-by generators became common, a name was needed to identify the wiring systems that they supplied.
As some others have stated, the wording of the definition may not be perfect, but I think the intent is clear. The key is the interpretation of the words "electrical connection".
Referring to the sketch below, the 480/277 volt service (System 2) ends at the dry-type transformer. The 208/120 volt system is separately derived (System 3) and both are required to be grounded.
They are completely separate systems in terms of any current flow from one to the other, because they are connected to each other at a single point, the ground bus (A) in the dry-type transformer. There is a "connection" but not one over which current can flow.
Any load and/or fault current originating from either transformer is confined to that system, and can only flow back to it?s point of origin. Live-to-enclosure faults (aka ground faults) in both systems are illustrated.
Other than the problem of clarifying the definition of an SDS, there is no technical or safety issue.
Comments are welcome.