Hi all, two questions:
- Is the working interpretation of 250.25 that the utility side transformer characteristics for a supply-side interconnected PV system must match the characteristics of the existing service?
- Example - a building has a 2000A 208/120V 3Ph 4W service from the utility. If the PV system on the roof utilizes 480/277V inverters, could a 480/277V - 208V step down transformer be used; that is, the utility side of the transformer is 208V 3Ph 3W delta and does not match the existing service
- 250.25 does not specifically state that the exact phase and neutral characteristics must match the service, but that they "comply with the requirements of 250.24(A) through (D)." This includes 250.24(C)(3), which includes provisions for a delta-connected service
- Using the above example, suppose a transformer is installed outside of a building. The POI is inside the building, the PV system is on top of the building. 250.30(C) states that "if the source of the separately derived system is located outside the building or structure supplied, a grounding electrode connection shall be made at the source location to one or more grounding electrodes in compliance with 250.50." Does the equipment grounding conductor (EGC) between the supply-side service disconnect, which is connected to the existing building grounding electrode system (GES) via a properly sized grounding electrode conductor (GEC), satisfy this requirement?
- This assumes that the primary side (utility side) and secondary side (PV side) grounding pads are electrically connected inside of the transformer by the manufacturer