Please forgive the invitation for a re-hash of old topics. I have spent some time this afternoon in the archives, and could not find anything which directly addresses my question.
First, some preliminaries for the benefit of my education:
According to bennie(member#800), the term 'separately derived system' (SDS) originally described systems totally isolated from the serving utility, and this definition still applies to these systems. His gripe is that this term has been extended to apply to other systems (transformers, in particular) which are not totally isolated. In theory, I agree with his point. By following the grounding requirements outlined in the NEC for SDS's, we introduce ground loops into our buildings.
Charlie(member #59), however, made the point that due to the very nature of our installations (metal conduit and building steel connecting everything) we already have ground loops, so we would do well to admit it and make the connections deliberate.
Is this a fair assessment of the beliefs regarding SDS's? If not, set me straight.
Now for the real question on my mind. For my purposes, the generator is permanent, not portable or vehicle-mounted. It is my understanding that 700.7(D) requires ground-fault indication under certain conditions, and that in order to provide this indication, use of a SDS is required.
Again, if I am off base, somebody call me out.
Finally, the question. Other than the above circumstance, does the NEC require a generator to be connected as an SDS? Even if not required, is there a good reason to do it?
First, some preliminaries for the benefit of my education:
According to bennie(member#800), the term 'separately derived system' (SDS) originally described systems totally isolated from the serving utility, and this definition still applies to these systems. His gripe is that this term has been extended to apply to other systems (transformers, in particular) which are not totally isolated. In theory, I agree with his point. By following the grounding requirements outlined in the NEC for SDS's, we introduce ground loops into our buildings.
Charlie(member #59), however, made the point that due to the very nature of our installations (metal conduit and building steel connecting everything) we already have ground loops, so we would do well to admit it and make the connections deliberate.
Is this a fair assessment of the beliefs regarding SDS's? If not, set me straight.
Now for the real question on my mind. For my purposes, the generator is permanent, not portable or vehicle-mounted. It is my understanding that 700.7(D) requires ground-fault indication under certain conditions, and that in order to provide this indication, use of a SDS is required.
Again, if I am off base, somebody call me out.
Finally, the question. Other than the above circumstance, does the NEC require a generator to be connected as an SDS? Even if not required, is there a good reason to do it?