I was reviewing Mike Holts DVD, Grounding Versus Bonding, about separitely derived systems, and looking at the definition for SDS, and I'm still not 100% sure what a SDS is. I have a good understanding how to ground and bond a SDS. I understand that a generator with a transfer switch that switches the hot and neutral conductors is a SDS. Can anyone explain what a separitely derived system is, or have an example?
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
Ice, since your a Florida guy, I'm guessing generators are your issue. Note below the key is no direct connection. For example a 4 pole transfer switch that will switch the grounded conductor.

08 said:
Separately Derived System. A premises wiring system whose power is derived from a source of electric energy or equipment other than a service. Such systems have no direct electrical connection, including a solidly connected grounded circuit conductor, to supply conductors originating in another system.
 