Separation of Distribution Equipment in Hospitals

Status
Not open for further replies.

mshields

Senior Member
Location
Boston, MA
Being from Mass and performing most of our work in Mass, we are accustomed to having separate, dedicated, 2 hour rated rooms for Emergency electrical distribution equipment. In hospitals, this means a dedicated 2 hour rated room for the Critical and Life Safety equipment.

I don't believe this is required by the NEC and therefore I imagine there are new hospitals out there that have Normal, Critical, Life Safety and Equipment gear all in the same room. And that this is perfectly code compliant.

Is that a true statement?

Thanks,

Mike
 
I don't believe this is required by the NEC. . . .
But it is required by NFPA 110, article 7.2. What that document calls the "Emergency Power System," which I believe includes the emergency branch ATS and its associated distribution panel, cannot be in the same room as normal branch equipment.

 