Building is 4 feet from house, but it is a seprate structure.
Pulled feeders, neutral and bonding jumper.... a branch circuit off of the meter can...... the sub panel was bonded to the service neutral. All of the wire sizes and disconnects where code compliant. We failed inspection based on the fact that we werent bonded to a seperate ground rod at the seperated building. The code has an exception stating that if the building is fed by a single branch circuit (to include a multiwire, single branch circuit). So why did we fail?
225.30
250.32
Pulled feeders, neutral and bonding jumper.... a branch circuit off of the meter can...... the sub panel was bonded to the service neutral. All of the wire sizes and disconnects where code compliant. We failed inspection based on the fact that we werent bonded to a seperate ground rod at the seperated building. The code has an exception stating that if the building is fed by a single branch circuit (to include a multiwire, single branch circuit). So why did we fail?