seperate circulator disconnecting means

Status
Not open for further replies.

sirhc

Member
Is a seperate disconnect required for boiler circulator pumps in addition to the boiler disconnect? Existing disconnecting means is a single pole switch, 500,000 btu boiler with fractional hp pumps. What code article?
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
2008 NEC 422.12, 422.12 Ex. No. 1 & 422.32.

Half a million BTU is a larger boiler. . . perhaps the pumps aren't "within sight" of the disconnect switch?
 