S sirhc Member Aug 4, 2009 #1 Is a seperate disconnect required for boiler circulator pumps in addition to the boiler disconnect? Existing disconnecting means is a single pole switch, 500,000 btu boiler with fractional hp pumps. What code article?
Is a seperate disconnect required for boiler circulator pumps in addition to the boiler disconnect? Existing disconnecting means is a single pole switch, 500,000 btu boiler with fractional hp pumps. What code article?
al hildenbrand Senior Member Location Minnesota Occupation Electrical Contractor, Electrical Consultant, Electrical Engineer Aug 4, 2009 #2 2008 NEC 422.12, 422.12 Ex. No. 1 & 422.32. Half a million BTU is a larger boiler. . . perhaps the pumps aren't "within sight" of the disconnect switch?
2008 NEC 422.12, 422.12 Ex. No. 1 & 422.32. Half a million BTU is a larger boiler. . . perhaps the pumps aren't "within sight" of the disconnect switch?