Seems like a lot more panels than necessary.
And you only have one line shown to each panel? That seems odd, but I'm not sure what your voltages are there.
Are all the panels only supplied with a single line-neutral supply? Is one pole of each of the two pole breakers for the neutral wire?
My guess is it is similar to what you see in European systems, maybe a 415/240 wye system. To each sublocation is just one phase and neutral. Having 6, 10, and 16 amp breakers in there suggests it is not an NEC application either, but the 40 amp kind of seems odd for IEC applications also.
If you use a ground fault circuit interrupter of suitable sensitivity instead, it is better.Subpanel main breaker could be 32Amp as per IEC...hope this getts me off the hook:happyno:
regards,
Mustafe
Outside of that most any other retails you seek approval on are outside NEC scope and this is primarily a NEC based audience here, most of us have no clue if your design is up to the codes/standards where this will be installed.
------------------------------------------------------------------------------------------------------------------------------------------------Why are you using 3Ph MCB’s for 1Ph loads? In the event of a fault in a single room three rooms will loose supply.
If this is to be done to BS7671 you need to revise the OCPD or the cable feeding each room. 63A is way too high for 4mm².
If you use a ground fault circuit interrupter of suitable sensitivity instead, it is better.