we have a cell tower with multiple meter loops coming from a single utility pole opposite cell site. our drawing shows a new service coming off new new transformer opposite side. This is what POCO said could be a no go
POCO reponse to new service.....The plan you sent shows a proposal to feed the new meter from a new transformer to be installed on the north side of the fire station. This might be possible, except that we believe the National Electrical Safety Code will not allow it for this reason. There would be multiple points of service on a single structure from widely separate sources, and on a metal structure. We do not believe this is acceptable.
i havent replied to email just yet but i do believe this is permitted 230.2 B 1 what do you guys think??
POCO reponse to new service.....The plan you sent shows a proposal to feed the new meter from a new transformer to be installed on the north side of the fire station. This might be possible, except that we believe the National Electrical Safety Code will not allow it for this reason. There would be multiple points of service on a single structure from widely separate sources, and on a metal structure. We do not believe this is acceptable.