Seperately Derived System Grounding
xformer
Dallas, Tx
Master Electrician
Does the GEC ran for a separately derived system have to be unspliced when connected to both a primary grounding electrode and as a bond to a secondary electrode? Put another way, does the GEC for the Separately Derived system have to be used as a bonding wire to the secondary grounding electrode?
(C) Continuous. Except as provided in 250.30(A)(5) and
(A)(6), 250.30(B)(1), and 250.68(C), grounding electrode
conductor(s) shall be installed in one continuous length
without a splice or joint. If necessary, splices or connections
shall be made as permitted in (1) through (4):
(1) Splicing of the wire-type grounding electrode conductor
shall be permitted only by irreversible compressiontype
connectors listed as grounding and bonding equipment
or by the exothermic welding process.
(2) Sections of busbars shall be permitted to be connected
together to form a grounding electrode conductor.
(3) Bolted, riveted, or welded connections of structural
metal frames of buildings or structures.
(4) Threaded, welded, brazed, soldered or bolted-flange
connections of metal water piping.