- Location
- Massachusetts
I just saw an unusual pipe material used as conduit on a feeder to a 400A safety switch. The 4" corrugated plastic pipe was a septic drain pipe, and the fitting at the switch enclosure was a 4" PVC plumbing elbow. This sure seems to be an NEC violating, but I cannot point to a reference other than 110.3(A)(1) on "suitable for installation." Is there a better NEC reference that prohibits installations like this, or is it actually acceptable to protect conductors in this manner? Thanks and Happy Thanksgiving.
Are the conductors within suitable for direct burial?
If so that would not be a raceway .... just a sleeve.