sparky1967
Member
- Location
- Seattle, WA, USA
I'm wiring up a new septic system at a cabin in a somewhat remote location. The system consists of a pump in the septic tank and a controller panel for said pump. The controller and the pump each call for a dedicated 20A circuit. The main panel is at one end of the cabin and the pump controller panel and disconnect are mounted to an exterior wall at the opposite end. Is there any reason I couldn't simply run some 10-3 romex under the cabin (nice big crawlspace) if I use a double pole single throw breaker in the main panel? (I'm running #10 due to distance of run to prevent excessive voltage drop).
This seems to be acceptable per NEC but wondering if there's a good reason not to do this.
Also, I have not been able to find a disconnect rated @ 20 amps. It appears that 430.110 (A) and (A)(2) both allow a higher rating, so that I could use a commonly available 30A disconnect or even a hot-tub 50A disconnect which can be had cheap at Home Depot.
This seems to be acceptable per NEC but wondering if there's a good reason not to do this.
Also, I have not been able to find a disconnect rated @ 20 amps. It appears that 430.110 (A) and (A)(2) both allow a higher rating, so that I could use a commonly available 30A disconnect or even a hot-tub 50A disconnect which can be had cheap at Home Depot.