I'm drawing a blank on code section that requires a disconnect in sight of the tank :weeping:
I would say 430.102 is where to start, and which subsection applies depends on exactly what you have.I'm drawing a blank on code section that requires a disconnect in sight of the tank :weeping:
Do all your well pumps meet the criteria for the Exception to 430.102(B)?I will put a breaker lock out kit in the panel on well pumps.
You may well (no pun intended) see something I don't, but I would not accept that based on 430.102. Can you direct me to the justification ?I will put a breaker lock out kit in the panel on well pumps.
You may well (no pun intended) see something I don't, but I would not accept that based on 430.102. Can you direct me to the justification ?
Where such a location of the disconnecting means for the motor is impracticable or introduces additional or increased hazards to persons or property
I have a well with submersible pump that is in 4 inch casing @ about 150 feet deep.
May or may not be impracticable to place a disconnect within sight of this motor, but I'm pretty sure it would involve increased hazards to be able to get to a disconnect within sight of this motor for most people, unless you know someone that can fit into a 4 inch tube.
No argument there, but most well pumps have a controller and, as best I decipher 430.102, a disconnect is needed for the controller.
Do all your well pumps meet the criteria for the Exception to 430.102(B)?
Roger
I have used breaker lock kits to comply with 422.31(B) also...
Sorry I didn't respond sooner.
So...in looking at 430.102(B)...I'm told to have a disconnect according to (B)(1) or (B)(2)...
The motor on wells is our area is hundreds of feet down in the ground out of sight of any disconnecting means for...
1. The motor (B)(1)
2. And the motor is also out of sight of the pressure switch (Controller) at the storage tank located in the basement of the dwelling (B)(2)
So I use a breaker lock kit to comply as allowed in the exception to (1) and (2)
To me, a septic pump would not fall under "Appliances" and, unless your "pressure switch (Controller)" was in sight from the branch circuit disconnecting means, I personally would still require a disconnect at the controller per 430.102 (A)
....I agree the controller disconnect is needed and I put a toggle switch at the well pump holding tank with the controller(pressure switch)
I have typically done this as well.
But now the question that comes to mind is this a violation, unless that toggle switch is a "lockable" type?
Regarding the "Controller" disconnecting means...it would NOT be required to be lockable if within sight.
There are many configurations of Overcurrent Device-Controller-Motor location that dictate the requirements for the disconnect means for each.
I was referring to a typical 2-pole toggle switch being used as a disconnecting means for a well pump. The switch disconnects power to the pressure switch (controller) which is adjacent to it and within sight.
The actual pump motor is buried inside of the well, 100 feet away, and 50 feet deep. No disconnect within sight there.