gndrod said:As Pierre states, SEU or SER cannot be below ground even in conduit.
I see this installation all the time...
gndrod said:As Pierre states, SEU or SER cannot be below ground even in conduit.
338.2 Definitions.gndrod said:Larry, please divulge your source on the "U" Tx
EEC said:Article 388 does not have the R behind SE. Can SER al Cable be installed in PVC conduit buried underground? What code section deals with SER
georgestolz said:Hello Don, and welcome to the forum.
Ben, did you check out the bunny trail I left on the first page? Essentially, the conclusion that was reached on the prior threads is that the term "Aboveground" is the opposite of "Underground." To the UL, "Underground" means directly buried. So, when they say "Aboveground" they mean "Not Directly Buried".
Absolutely. Just as with the AC whip debate, a conduit is not a location. If the conduit is outdoors, underground, in a wet location, etc., so are the conductors within.Pierre C Belarge said:The inside of a raceway below grade cannot be construed as aboveground.
My source was this letter, to Mike Whitt from Austin Wetherell from the UL. To be honest, looking back at my post, I did add my own twist to what was written. Thanks for calling me on that.Pierre C Belarge said:George
Where did you exactly read that? Or do you know someone in UL who specifically told you this.
If you read the wording without any twisting, it says the cable is for aboveground... to me the raceway below grade is not aboveground.
In can be construed, as I did in my last post. But that doesn't make me right. I'm gonna ponder this some more.I do not understand the reasoning for debating this simple point????????
The inside of a raceway below grade cannot be construed as aboveground.
One thing, to share this headache I've got:Pierre C Belarge said:If you read the wording without any twisting, it says the cable is for aboveground... to me the raceway below grade is not aboveground.
That 'U' he's talking about is a prefix, and does stand for underground as a prefix. When added as a modifier, or a suffix, it does not.georgestolz said:My source was this letter, to Mike Whitt from Austin Wetherell from the UL. .