This code quandaries (4th question) article spurred some conversation with some co-workers and we are in disagreement on calculating the ampacity for SER cable ran for sub feeds to panelboards indoors in the same single family dwelling.
http://www.ecmweb.com/mag/electric_code_quandaries_18/index.html
Some of the electricians at work and on the forums are saying that SER can be approved for table 310.15(B)(6) ampacity and AHJ's routinely do this. I say no and in my experience they dont.
I'm curious as to the change in code from 1999 to 2005 on SER cable ampacity. In the 1999 code sec. 338.4(a) says SE type cables will be subject to the ampacities of sec. 336.26.
In 2002 or 2005 that language apparently changed... 2005 now states in sec.338.10(B)(4)(a) SE is subject to parts 1 and 2 of 334 excluding334.80.
My question is two parts....
1.) Why was the requirement for the 60C ampacity column for SER apparently removed?
2.) Would an inspector be correct in allowing table 310.15(B)(6) for SER cable indoors for sub feeds?
http://www.ecmweb.com/mag/electric_code_quandaries_18/index.html
Some of the electricians at work and on the forums are saying that SER can be approved for table 310.15(B)(6) ampacity and AHJ's routinely do this. I say no and in my experience they dont.
I'm curious as to the change in code from 1999 to 2005 on SER cable ampacity. In the 1999 code sec. 338.4(a) says SE type cables will be subject to the ampacities of sec. 336.26.
In 2002 or 2005 that language apparently changed... 2005 now states in sec.338.10(B)(4)(a) SE is subject to parts 1 and 2 of 334 excluding334.80.
My question is two parts....
1.) Why was the requirement for the 60C ampacity column for SER apparently removed?
2.) Would an inspector be correct in allowing table 310.15(B)(6) for SER cable indoors for sub feeds?