mkgrady
Senior Member
- Location
- Massachusetts
I'm running a feeder from a generator to a transfer switch that will be downstream from a 100 amp CB on the generator. The cable will run a few feet through insulation. I think the prior code cycle would require using the 60 degree rating and 1/0 AL. Am I correct that I can use the 75 degree column and that #1 AL SER is good for 100 amps?