can i install 2/3 ser cable in 2 inch pvc underground for a barn feeder. is there any issues with heating . will feed a 60 amp subpanel
augie47 said:most likely you can do it ! :smile:
will it meet the requirements of the NEC ? NO WAY NEC 338.12
wbalsam1 said:I can't wait until NY gets on the '08 NEC.
marissa2 said:This question came up today in a CEU class, the instructors answer was that SER is not listed for a wet location. On the side of a house is OK but not underground. By the way the instructor was the head state electrical inspector.
Lou
marissa2 said:This question came up today in a CEU class, the instructors answer was that SER is not listed for a wet location. On the side of a house is OK but not underground. By the way the instructor was the head state electrical inspector.
Lou
2008 NEC said:338.12 Uses Not Permitted.
(A) Service-Entrance Cable. Service-entrance cable (SE) shall not be used under the following conditions or in the following locations:
(1) Where subject to physical damage unless protected in accordance with 230.50(A)
(2) Underground with or without a raceway
(3) For exterior branch circuits and feeder wiring unless the installation complies with the provisions of Part I of Article 225 and is supported in accordance with 334.30 or is used as messenger-supported wiring as permitted in Part II of Article 396
thats whats inside ser cable . just skin it?iwire said:As much as I have fought about SER not being directly prohibited from running in an underground raceway I can not in good conscience tell you to go for it. Use some XHHW or THWN etc.
mpd said:UL white book lists SE cable for aboveground use, the 08 code makes it very clear, i have never permitted it
Maybe, maybe not, but that's an expensive way to do it. "Mobile home feeder cable" or individual XHHW's would be cheaper.shockerz said:can i install 2/3 ser cable in 2 inch pvc underground for a barn feeder. is there any issues with heating . will feed a 60 amp subpanel
mpd said:iwire
IMO it was never permitted, and I failed many contractors for it
They've already got rules about that sort of thing.mpd said:iwire
maybe they realized the cable was being used in violation of the listing, just a thought