ser cable

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
As much as I have fought about SER not being directly prohibited from running in an underground raceway I can not in good conscience tell you to go for it. Use some XHHW or THWN etc.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
most likely you can do it ! :smile:
will it meet the requirements of the NEC ? NO WAY NEC 338.12
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
wbalsam1 said:
I can't wait until NY gets on the '08 NEC. :)

I happened to have '08 on my desk when I read the post.
I will say, '08 makes it more clear than '02.
 

marissa2

Senior Member
Location
Connecticut
This question came up today in a CEU class, the instructors answer was that SER is not listed for a wet location. On the side of a house is OK but not underground. By the way the instructor was the head state electrical inspector.
Lou
 

iwire

Moderator
Staff member
Location
Massachusetts
marissa2 said:
This question came up today in a CEU class, the instructors answer was that SER is not listed for a wet location. On the side of a house is OK but not underground. By the way the instructor was the head state electrical inspector.
Lou

That is also what the instructor at my class said.

'The outside of a house is not a wet location' :rolleyes:
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
marissa2 said:
This question came up today in a CEU class, the instructors answer was that SER is not listed for a wet location. On the side of a house is OK but not underground. By the way the instructor was the head state electrical inspector.
Lou

Marissa here is the 2008 code

2008 NEC said:
338.12 Uses Not Permitted.
(A) Service-Entrance Cable. Service-entrance cable (SE) shall not be used under the following conditions or in the following locations:
(1) Where subject to physical damage unless protected in accordance with 230.50(A)
(2) Underground with or without a raceway
(3) For exterior branch circuits and feeder wiring unless the installation complies with the provisions of Part I of Article 225 and is supported in accordance with 334.30 or is used as messenger-supported wiring as permitted in Part II of Article 396
 

shockerz

Member
Location
southern ct.
iwire said:
As much as I have fought about SER not being directly prohibited from running in an underground raceway I can not in good conscience tell you to go for it. Use some XHHW or THWN etc.
thats whats inside ser cable . just skin it?
 

mpd

Senior Member
UL white book lists SE cable for aboveground use, the 08 code makes it very clear, i have never permitted it
 

iwire

Moderator
Staff member
Location
Massachusetts
mpd said:
UL white book lists SE cable for aboveground use, the 08 code makes it very clear, i have never permitted it

It seems like if it was already prohibited they would not have had to change the NEC. :grin:
 

mdshunk

Senior Member
Location
Right here.
shockerz said:
can i install 2/3 ser cable in 2 inch pvc underground for a barn feeder. is there any issues with heating . will feed a 60 amp subpanel
Maybe, maybe not, but that's an expensive way to do it. "Mobile home feeder cable" or individual XHHW's would be cheaper.
 

iwire

Moderator
Staff member
Location
Massachusetts
mpd said:
iwire

IMO it was never permitted, and I failed many contractors for it

I know thats how you feel and what you did, I don't forget much. :cool:

I also know they do not change the NEC for no reason.

I recently went to my continuing education class, taught by a pair of inspectors. One them read the change and a student said "Yeah except for temporary use" Both inspectors laughed and said well yes of course. :grin:
 

mpd

Senior Member
iwire

maybe they realized the cable was being used in violation of the listing, just a thought
 