inspector141 said:
In the 05 code article 338.10(B), there are two areas where se cable is allowed. 1. Interior 2. Exterior. If the ser cable is not identified for underground installation, I don't know how it could be allowed. Exterior and underground are two totally different installations. Also, would the ser installation be condidered a sleeve or a complete conduit system? I would not allow ser cable to be pulled in a long conduit system, inside or outside, when there are say two or three bends in the conduit. Too much tension and friction in my view.
In the 08 code, case closed. 338.12
I don't see anything that prohibits pulling it in a long conduit system (above ground) providing that the conduit and bends are correctly sized. The 05 and 08 codes allows cables to be installed in many conduit types, where it is not prohibited by the relevant cable article (for example, 352.22 for PVC conduit). Why you might choose to do this for a long run is another story.
I used to think SER was OK underground in conduit because cables in conduit underground need to be suitable for wet areas, and SEU/SER are routinely installed in wet areas. I thought 05 left the door open on this, and I'm happy that 08 makes it clear. The 07 UL white book is equally clear. I don't know what earlier editions of the UL white book say. Perhaps they closed what I thought was an open door in 05.
I was reviewing the protection requirements for SE cable in 08. 338.12(A)(1) refers to protection in accordance with 230.50(A). But 230.50(A) is specifically for
underground service-entrance conductors, and it is 230.50(B) that deals with all service entrance conductors
other than underground. It looks to me like the reference is a typo. Anyway, 230.50(B)(1) specifically allows SE cable above ground in specific types of conduit for protection, and doesn't place any limitations on the length of the conduit.
Dave