NEC 2008 clarifies that Table 310.15(B)(6) can only be used for cables that carry 100% of the dwelling unit load. Also 338.10 (B)(4) that it must comply with with requirements of Part 2 of 334. Section 334.80 Ampacity shall be in accordance with 60 degrees C.
For the interior wiring from a 200amp main disconnect to a service panel or from a 100 amp breaker in a service panel to a interior sub-panel,using aluminum conductors I would need 300mcm for the service panel and 1/0 for the sb-panel correct ?
For the interior wiring from a 200amp main disconnect to a service panel or from a 100 amp breaker in a service panel to a interior sub-panel,using aluminum conductors I would need 300mcm for the service panel and 1/0 for the sb-panel correct ?