can i put ser cable in conduit to protect it.  it will only be about 6 ft of the 20 ft length.
	
		
			
		
		
	
				
			Do you mean the same size? No but you can get ser with a full size neutral/ground. Be very carefull here-- what size is the bare conductor? and what size are your phase conductors?thanks. it is for a 3 phase service, so does the nuetral coming in have to be the same as the 3 hots
That's plenty (for 150a if aluminum), unless you have zero line-to-line loads.it is a 3 condutor( 4/0 ) and a bare 2/0 ground
				