I am installing a 125A SqD QO MLO subpanel. It will feed a 50 amp range and the counter plugs. As well as a bathroom. And 2 x 1/6 HP Grundfos hydronic heat pump circulators. The run is 80 feet. I want to use 1/0 Al SER.
The load is
50A or 12,000kw
3 x 20A
2 x 5.5 motors.
So roughly 90A per phase.
I want to confirm I am good to use the 75* tables as its SER and the lugs on the panel and the Eaton CH breaker are rated 75* at the terminals. And I can go to the next highest standard breaker which would be a 125A.
The load is
50A or 12,000kw
3 x 20A
2 x 5.5 motors.
So roughly 90A per phase.