If I say the condition for Type NM below applies to Type SE, does it apply?
One difficulty of your interpretation, that the 338.10(B)(4)(a) phrase "installation requirements of Part II of Article 334, excluding 334.80" means only those sections of Part II of Article 334 that don't specifically refer to type NM cable, is that 334.80 itself refers to type NM cable. So since the authors included the phrase "excluding 334.80" in 338.10(B)(4)(a), it means they expect that the preceding language in 338.10(B)(4)(a) would include 334.80, i.e. that it includes sections of Part II of Article 334 that do specifically refer to NM cable.They could say...
Type SE service-entrance cable used for interior wiring shall comply with the installation requirements of Part II of Article 334 for Type NM [or NMC, or NMS], excluding 334.80.
We are not going to agree on this. There is no reason for the NM article to reference other cable types. The SE article does that. All of the rules in Part II of Article 334 apply to where it is being used for interior wiring. For all practical purposes the rule in 338 is saying that SE becomes NM where used in an interior location.
For all "intents and purposes" I agree with you both. But I have a hard time with it if we get into literal interpretations.It applies, I have never seen anyone question it.
Would it be your opinion that if I use SE for inside feeders (and we do) that no rules in 334 apply?
All takes me back to post #4 and trying to visualize a compliant install.
392.6(H) requires the tray be accessible, 334 prevents SE from being used above a drop or suspended ceiling so what's left.
Because the code says soI can't see it being compliant however if a cable tray is installed and all the cables installed in it are nm and ser then I really don't see why it needs to be accessible. Basically it is just an easy method to lay the cables to perhaps avoid drilling joists. Hopefully the op will chime in
Can the cable tray be used as a "chase" without being subject to the requirements of 338?Basically it is just an easy method to lay the cables to perhaps avoid drilling joists. Hopefully the op will chime in
Yeah-- that's the catch.. So if I install a short piece of gutter-- no ends-- as a sleeve to lay wires in then I would not have to have it accessible.Because the code says so
Exposed and accessible except through partitions and walls [392.18(E)].The cable tray is being used as a means of support. The construction of the deck is steel.
So, Art. 392 requires access to the cable tray. Would this requirement be for the entire span?
Typo, I meant article 392. WayneCan the cable tray be used as a "chase" without being subject to the requirements of 338?
Note the heading on 334.12 Uses NOT permittedI think that the code allows SE cable exposed in the dropped ceiling, if it is a multifamily dwelling.
334.12(A)(2) Exposed in dropped or suspended ceilings in other than one- and two-family and multifamily dwellings.
The way he wrote it up seems contradictory, but when you take into consideration 334.12 is uses not permitted, exposed in dropped or suspended ceilings of multifamily buildings is permitted.Note the heading on 334.12 Uses NOT permitted