SER in conduit

Status
Not open for further replies.

czars

Czars
Location
West Melbourne, FL
Occupation
Florida Certified Electrical Contractor
Is it acceptable to use SER conductors in conduit with the sheath removed? I do not believe that the individual conductors are marked.
 
No, you are not allowed to strip a cable and use the individual conductors unless each conductor has the required markings.
 