C czars Czars Location West Melbourne, FL Occupation Florida Certified Electrical Contractor Mar 5, 2021 #1 Is it acceptable to use SER conductors in conduit with the sheath removed? I do not believe that the individual conductors are marked.
Is it acceptable to use SER conductors in conduit with the sheath removed? I do not believe that the individual conductors are marked.
Coppersmith Senior Member Location Tampa, FL, USA Occupation Electrical Contractor Mar 28, 2021 #2 No, you are not allowed to strip a cable and use the individual conductors unless each conductor has the required markings.
No, you are not allowed to strip a cable and use the individual conductors unless each conductor has the required markings.
Fred B Senior Member Location Upstate, NY Occupation Electrician Mar 28, 2021 #3 In fact code calls for a minimum that cable sheath must enter box beyond connector.
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Mar 28, 2021 #4 Are you installing this underground? Can the sheath be left on in the conduit?