You can't have a non-fused service disconnect and remote overcurrent protection (OCP). Has to either be a fused disconnect or non-fused with OCP immediately adjacent thereto.... But if I use SER (AL 4/0) cable with an outer jacket, 3 insulated conductors and a bare ground, how would I correctly use the ground in the cable from the panel on the "2nd" floor all the way to the Ground rod? I do understand that certain utility providers may have a preference, but of course the AHJ supersedes and I would like to know about providing the ground from the panel to the ground rod as I know this is more often preferred over bonding at the service disconnect (non-fused). Again, much thanks.
Not sure what you mean by 'deflection formulas'.
Conduit fill is simply 53%. Cable area is pi*D?/4, where D is the widest cable dimension.
You also have pull requirement(s) of 314.28.
***
I suppose I should have mentioned this earlier, but we could make the LB a moot discussion if OP just terminates the PVC at one of the sill plate covers posted by iwire. Bending radius requirement must still be met, but shouldn't be a problem with a full size, perhaps even slotted hole under the sill plate cover.
Wow, this is great! Thanks. To follow up I'll say that no, there is no copper in the house, or building steel for that matter. I will definitely drive 2 ground rods and will also scrub the idea of using the LB and instead use an 8x8x4 PVC JB. Also, yes, the entrance into the building would only be a stub into the joists and then free cable up into the panel one flight up. It's a modular home and already has a 2" PVC sleeve from the "basement" sacrifice floor up into the panel. But if I use SER (AL 4/0) cable with an outer jacket, 3 insulated conductors and a bare ground, how would I correctly use the ground in the cable from the panel on the "2nd" floor all the way to the Ground rod? I do understand that certain utility providers may have a preference, but of course the AHJ supersedes and I would like to know about providing the ground from the panel to the ground rod as I know this is more often preferred over bonding at the service disconnect (non-fused). Again, much thanks.
230.90
I think I'm starting to blog myself....