Used a piece of SER from the load side of the meter socket to the adjacent panel in a house. I snipped off the uninsulated conductor at each end since only 3 wires were needed. AHJ is telling me that it needs to be replaced because the uninsulated conductor must be landed at the neutral bar even though it is not being used for anything. I can't find an NEC reference requiring this. Am I missing something?