SER&UF in same conduit

Status
Not open for further replies.

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
Question..
UF is a Chapeter 3 wiring method. Is seperation still required if its a class 2 system?

I would say no separation required, they could be in the same raceway.

725.136 Separation from Electric Light, Power, Class 1,
Non–Power-Limited Fire Alarm Circuit Conductors,
and Medium-Power Network-Powered Broadband
Communications Cables.
(A) General. Cables and conductors of Class 2 and Class 3
circuits shall not be placed in any cable, cable tray, compartment,
enclosure, manhole, outlet box, device box, raceway,
or similar fitting with conductors of electric light,
power, Class 1, non–power-limited fire alarm circuits, and
medium-power network-powered broadband communications
circuits unless permitted by 725.136(B) through (I).

I am sure there will be some debate about this.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I would say no separation required, they could be in the same raceway.

725.136 Separation from Electric Light, Power, Class 1,
Non–Power-Limited Fire Alarm Circuit Conductors,
and Medium-Power Network-Powered Broadband
Communications Cables.
(A) General. Cables and conductors of Class 2 and Class 3
circuits shall not be placed in any cable, cable tray, compartment,
enclosure, manhole, outlet box, device box, raceway,
or similar fitting with conductors of electric light,
power, Class 1, non–power-limited fire alarm circuits, and
medium-power network-powered broadband communications
circuits unless permitted by 725.136(B) through (I).

I am sure there will be some debate about this.
I think someone mentioned the controls were 240 V. That would make them Class 1 conductors.
 

Strombea

Senior Member
I think someone mentioned the controls were 240 V. That would make them Class 1 conductors.
I don't know how they determine 120 or 240 because nothing in the control system is actually using 240 volts. The wires are 120 to neutral. But maybe it's a "potential" thing. But if only one phase was there it would magically be considers 120v?
I would consider them 120v wires because you actually could have a 208v wire to neutral on a delta high leg so I'm assuming the potential to neutral is enough for classification
 