Good point.Originally posted by Minuteman:
However, you shouldn't need a EGC in a service riser.
What would the size of the conductor have to do with harmonics, or with the price of Tea in Bulgaria, anyway?Originally posted by Minuteman:I did not even think using the 4/0 since some people get all freaked out about harmonics.
Not just in this forum, but every time I have been in a conversation with PE's about parallel SERVICE conductors in the same conduit, the next thing that is said is, "Harmonics". So, I thought I would play it safe this time and not bring it up.Originally posted by charlie b:
What would the size of the conductor have to do with harmonics, or with the price of Tea in Bulgaria, anyway?Originally posted by Minuteman:I did not even think using the 4/0 since some people get all freaked out about harmonics.
Huh?Originally posted by Minuteman:
Not just in this forum, but every time I have been in a conversation with PE's about parallel SERVICE conductors in the same conduit, the next thing that is said is, "Harmonics". So, I thought I would play it safe this time and not bring it up.Originally posted by charlie b:
What would the size of the conductor have to do with harmonics, or with the price of Tea in Bulgaria, anyway?Originally posted by Minuteman:I did not even think using the 4/0 since some people get all freaked out about harmonics.
Pierre probably did not notice that your installation was a single phase.Originally posted by pierre:
Without considering for harmonics, you will have a minimum of 6 current carrying conductors per conduit. 310.15(B)(2(a) shows you will need to adjust for 80%.
What this is saying is if you had a 208Y/120 service or feeder that supplied a lot of nonlinear loads (think computers and other electronics) the neutral would have to be counted as a current carrying conductor for purposes of derating.310.15(B)(4)(c) On a 4-wire, 3-phase wye circuit where the major portion of the load consists of nonlinear loads, harmonic currents are present in the neutral conductor; the neutral shall therefore be considered a current-carrying conductor.
That will do it if the calculated load is less than 760 amps.Originally posted by tim:
Single phase 120/240 volt. I believe my solution is 2 3" risers. 500 mcm. Also, this is a 12 unit apartment building.
Originally posted by Minuteman:
A while back, I was hired to upgrade a outdoor 1200 amp, 120/240 Single phase MDP to a 1600 amp, 120/240 Delta 3 phase.
They had six 200 amp, single phase subpanel mains in the old MDP and added three 125 amp, 3 phase A/C units.
Originally posted by iwire:
Pierre probably did not notice that your installation was a single phase.