Re: sercvice conductor size

Originally posted by Minuteman:
My point has been over labored. But, all I was saying was... The Inspector, the City Engineer, the PE that I was referred to, and Pierre all brought up the question about harmonics. Not me.

True, there are still some single phase loads in my application. However, the topic in discussion is harmonics.
OK

I still suggest you take a look at Georges link it may help you out.
 
Re: sercvice conductor size

If the 75* column is used in 310.16 than use 600kcmil = 420amps. So the parallel 3" GRC would handle the 600kcmil as well.

BTW thanks George, I will print that out and read it later today. Perhaps whilst upon the throne. :D
 
Re: sercvice conductor size

Originally posted by Minuteman:
If the 75* column is used in 310.16 than use 600kcmil = 420amps. So the parallel 3" GRC would handle the 600kcmil as well.
I agree he can do that, but it is likely he can use the 500 and save some money if the load is less than 760 amps.

310.16, 500 CU @ 75C = 380 amps x 2 = 760 amps.

240.4(B)

Originally posted by Minuteman:
I will print that out and read it later today. Perhaps whilst upon the throne. :D
A great place to do important reading. :D
 
Re: sercvice conductor size

Sorry this took so long. The total load for the building is 625 Amps. These are only small 1 bedroom units 520sq ft. Thanks for all the input.
 
Re: sercvice conductor size

Originally posted by tim:
Sorry this took so long. The total load for the building is 625 Amps.
Is it too early for me to be doing math, or could be use parallel 350 AL, 700 amp fuses, and be fine?
 
Re: sercvice conductor size

Originally posted by georgestolz:
Originally posted by tim:
Sorry this took so long. The total load for the building is 625 Amps.
Is it too early for me to be doing math, or could be use parallel 350 AL, 700 amp fuses, and be fine?
George I know you are not using Table 310.15(B)(6) as an ampacity chart right? ;)

I think you misread 310.16 as two sets of 350 AL at best results in a total ampacity of 500 amps.

In AL you would need two sets of 600 kcmil minimum for the 625 amps of load.

Going back to copper two sets of 400 CU would provide a capacity of 670 amps and could be fused at 700 amps.
 
Re: sercvice conductor size

I mistakenly typed 350, I meant 250. :D

My wife was rushing me off, I goofed. I also didn't have time to show my math.

I've got 205 amps on 250 MCM AL per 310.16.
I've got 6 conductors per pipe (4 hot, 2 neu).
I've got 2 conduits.
205 x 4 = 820 amps

I've got to derate that:
205 x .8 = 164 amps per ungrounded conductor
164 x 4 = 656 amps

700 amp fuse.
 
Re: sercvice conductor size

But actually, he'd be over on pipe fill unless he used a smaller neutral in each parallel run.

If all the conductors were the same size, in 2.5" RMC, then his only option would be 3/0 CU, which would squeak into the fill tables and give him 640 amps to use.

edit to correct "640" - typed from memory :p

[ January 05, 2006, 08:45 AM: Message edited by: georgestolz ]
 
Re: sercvice conductor size

I'll try: How about using the 800 amp load 3phase, using three 2 1/2" conduits with four 400 Kcmil 75 degree Celsius column (table 310.16) thhn,in each conduit.The GEC will be 3/o. Man that Iwire is fast on the draw. Single phase OK: Load 625 amps, two 2 1/2" conduits w/three 400Kcmil in each conduit.GEC 2/o

[ January 05, 2006, 06:53 PM: Message edited by: Jhr ]
 
Re: sercvice conductor size

Originally posted by tim:
George, I am not using 2.5" pipe. Will be using 3".
In that case, the four parallel runs of 250 MCM AL would fit, if you were so inclined.

Copper is expensive but commands respect among many here. :)

It's up to you.
 
Re: sercvice conductor size

now now hold on a min please i was reading thru this part did someone say going fromsingle phase to three phase delta ?? if so. you have to watch out the single phase load vs 3 phase load because slecting the wires will get very tricky here.

I went thru that headache before


Tim is this installment is single phase if so i might miss this other wise if 3 phase service to the place you are wiring it most POCO will not hook up delta service anymore unless specal approval have to run in wye format

please let us know excat answer

if there please excuse moi for this one :D


Merci , Marc
 
Re: sercvice conductor size

thanks George for head up with the oringal question i know i got little lost here with so much feedback and alot of good info here.


Tim:

I can see what you mean being a single phase service for 12 plex apt set up but one question how you can come up with load demand for each apt ???

i know there is a " magic number " but i really can't point where i did see it but for myself i came up some figures for ave figures for small to med size apt i use 50 amp per apt and came up with 600 amp but you were wise to go little bigger service there. i will stick to 800 amp service if possible

for 600 amp service you can use 350KCM wires [X 2 ] in parallel set up with 3.5 inch rigid pipe the reason i slect slightly bigger than it should because it is easier to snake the wires in the same time you can bump up to 500 KCM if need to go to 800 amp service but really for 800 amp serivce it is wise to go with 4 inch conducts


merci , Marc
 
Re: sercvice conductor size

Originally posted by georgestolz:
Copper is expensive but commands respect among many here. :)
For me it is just habit like I imagine AL is habit for you. I have nothing against AL other than it's lower scrap value. ;)

Both have advantages and disadvantages.

For better or worse almost all jobs we take on have specifications that require all copper conductors.

I used copper SE on my own homes service for one reason only. The copper cable is smaller than its AL equal so it is less obtrusive.
 
Re: sercvice conductor size

Specs require all copper conductors. Also, I did not do the load calculations. The engineer did all that for me. The reason the load might seem a little high for each unit is that they are heated with three baseboard heaters and have a small electric water heater. No laundry.
 
Re: sercvice conductor size

Originally posted by frenchelectrican:
i know there is a " magic number "
Marc, I don't think there really is. :)

A load calculation is such a one-time, involved process, that trying to find a magic number would waste time, IMO. There's no safe, practical purpose for such a number, unless you're guessing at what size conduit to install for future use.

In many cases even the conduit size is spec'd in the plans. :)
 