jimmyglen
Senior Member
- Location
- St. Louis, Missouri
My very smart code instructor gave us a question on a SERVICE calculation for an office
We were asked to size the service and determine total load in VA
We were told the sq ft with 615 duplex recpt, 110' of multi outlet assembly etc etc etc
We were also given (4) 20 AMP CONT. USE BRANCH CIRCUITS as a part of the total load (we were told that this WAS NOT a recpt load and not subject to demand factors)
It was my thought that we should take the 20 amp x 1.25 and then times the voltage (120v) --- I cited Art 220.12A ---that would give us 4 x 2400va x 1.25
my instructor told that that since you cant put an actual 20 amp load on a 20 amp circuit that our calculation should be like this
4 x 1920Va x 1.25
citing Art 210
After thinking about this WAY too long, I decided that really its just bad practice to give a branch circuit load and not a specific load (or at least the branch circuit load should be a recpt load)
What say you?
We were asked to size the service and determine total load in VA
We were told the sq ft with 615 duplex recpt, 110' of multi outlet assembly etc etc etc
We were also given (4) 20 AMP CONT. USE BRANCH CIRCUITS as a part of the total load (we were told that this WAS NOT a recpt load and not subject to demand factors)
It was my thought that we should take the 20 amp x 1.25 and then times the voltage (120v) --- I cited Art 220.12A ---that would give us 4 x 2400va x 1.25
my instructor told that that since you cant put an actual 20 amp load on a 20 amp circuit that our calculation should be like this
4 x 1920Va x 1.25
citing Art 210
After thinking about this WAY too long, I decided that really its just bad practice to give a branch circuit load and not a specific load (or at least the branch circuit load should be a recpt load)
What say you?