The graphical representation is badly made for what it attempts to illustrate. The voltage readings around the circuit should be taken from point to point around the circuit and the sum of the individual voltage readings around the circuit should add up to the voltage that is read at the source terminals, so the voltage across the source terminals should be 119.2V instead of 0.8V. (Is this drawing saying that it is completely safe to touch the outgoing terminals of a loaded circuit at 0.8V? My practical experience says otherwise. ) It is based on Kirchhoff's Second Law. The showing of the 16A in two places is unnecessary. Kirchhoff's First Law.
Not correct. It is not just the transformer inefficiency as you proposed.My official position is that the loss is real, but is essentially seen as a loss due to transformer inefficiency.
I stopped before by just saying you were introducing more technically incorrect information. Now it appears the chickens have come home to roost in the post below so I thought I would add another 2 cents.Since the secondary is constructed of wire that has resistance, that .8V is lost getting to the very center of the secondary. Essentially, the ends of the conductor extend internally into the transformer to the center of the winding.
Let me see if I can simplify it: The sum of voltages around a loop equals zero. If you sum the voltages in the diagram you don't get zero you just get all the voltage drops. What is missing is the EMF source (the voltage rise) that produces these voltages across the resistors displayed.I am having a hard time cyphering through the "Engineer speak" on this thread.
Wrong. Most reasonable persons dealing with supply issues need to understand voltage regulation. Source impedance is a significant concern and should not be ignored. You will have to face transformers and burdens and adequate voltage supply sooner or later.Whether the power supply is drawn with a circle and a sine wave, a little battery symbol, or (what I consider) misrepresented with a resistor in a circle, this drawing has no bearing on knowledge that any reasonable person needs.
That is where George's "official position" has led to misunderstandings. It is not just the short lead length. It is the impedance even further upstream as well. In a simple representation, we use a Thevenin equivalent circuit model to represent what is upstream of the load. The Thevenin representation is a voltage and resistor in series.I agree with you George that the meter should read a nominal 120 volts. For any practical purpose that is all that is important. No one drawing this diagram would have any reason to get in to the properties and resistances of the short length of leads from the "generator" of power to the output terminals.
I did. At least twice.My conclusion is that the drawing is just plain wrong. Other than Mr. Wessel, and you George, was there anyone else who actually said this?
Point taken. I guess it would depend on the audience. But seeing as how the graphic was going to be used, it should be corrected so as not to create a stumbling block for those wanting to advance in the future.To cloud a series circuit representation by showing the internal resistance of the power supply as a factor in the circuit is unwise in my mind. If I were teaching a group of future electricians this subject matter, I would be thrilled if they actually grasped the concept that a switch with a high resistance is in series with a light load and as such will cause the light to dim and they understood why. That would be a good day!
As long as the load impedance is large compared to the source (i.e. the load is relatively small) source impedance is not a significant issue. As we know, that is not always the case.Frankly, I have done my share of troubleshooting and repair and supervision of others and have never cared about upstream losses or resistance yet.
Where would I connect a voltmeter to find that reading though?
(I appreciate the speedy replies, got to be comfortable explaining this tomorrow. )
Edit: It's strictly theoretical, right?
0.5 ohm is a more reasonable value for the source resistance of a typical wall outlet. You might get 0.05 taking the 120v off right at the load center. For my house it's about 0.01 but the transformer is right outside.
The least I can say is that a knowledgeable proofreader is needed.
If 3/4ths or more of cognizant people seeing this are mislead, it's bad.It's not so much proofreading as the graphic is not clear.
Look close. The probes that read 0.8 volts are INSIDE the power supply measuring the voltage across a 'resistor'. If the probes were outside the power supply they would see 119.2 volts.
If 3/4ths or more of cognizant people seeing this are mislead, it's bad.
And some voltage sources have negative impedance: the voltage increases slightly with increasing current.
Arc, also, have negative incremental impedance.
It depends on the accuracy you want. Perfect accuracy = infinite labor.So, internal resistance isn't confusing enough, you have to go through internal impedance in as well???
It depends on the accuracy you want. Perfect accuracy = infinite labor.