We have a 1600A EATON MDP. There will be a 200a feeder from MDP to a 200a SQD sub panel. IS there anything as far as Series rated equipment is there something we need to look into as far as SCCR? Can different brands of equipment be used in series?
The proper terminology is not sccr but AIC for circuit breakers and other overcurrent protection devices like fuses. Short circuit current rating indicates the amount of short circuit current a device can take without some specified level of damage. Amps interrupting capacity is how much short circuit current the overcurrent protection device can open.We have a 1600A EATON MDP. There will be a 200a feeder from MDP to a 200a SQD sub panel. IS there anything as far as Series rated equipment is there something we need to look into as far as SCCR? Can different brands of equipment be used in series?
Occasional exception - like Milbank or Midwest meter-main-loadcenter units. Just installed a Milbank recently, factory installed main breaker was a Siemens breaker. Label lists about every 1 inch wide plug on breaker made as acceptable to use for branch breakers.But to answer your question directly, no. Nobody does series ratings with competitor's products. Those ratings are attained through very expensive destructive testing and there is zero ROI on one mfr. testing a competitor's products down stream or up stream of their own.