Long time reader, first time poster.
I'm currently doing a short-circuit study at a location. We have a combination where the upstream breaker is rated 100 kAIC and the downstream breaker is rated 22 kAIC with ~58 kA of fault current. Luckily, that combination is series rated to 100 kAIC so we were good to go (consultant is fine with series rating). However, the plant didn't have the 100 kA breaker on hand, so they swapped in the 200 kA version. Same frame, same trip unit, same TCC... but, the 200 kAIC hasn't been tested with the 22 kAIC breaker. So, I'm losing my series rating.
I think I read somewhere that if you have a tested, series rated combination, that test can be applied to other breakers that share the same TCC even if they are not the exact same breaker. But, I can't find the standard now. Does this sound familiar to anyone? It makes common sense to me, but I need to find a specific reference for the inspector.
Thanks!!!!
Thanks!!!!