Hi all. This is my first post so please take it easy on a newbie :smile:
I'm currently working on a small retail shop and experiencing a problem. The main switchboard (existing) has an AIC rating of 57 KAIC. Using this figure, I arrived at 39KAIC at my 100A, 277/480V panel. Using the calcs., I spec'd the panel with an AIC rating of 42 KAIC. Now, our specifications allowed the panels to be series rated. I recently found out that the contractor has installed a 14 KAIC rated panel. At first glance, I don't believe this will work (not only that, it's not conforming to my design). Unless I can come up with supporting documentation, I believe the project will get red tagged by the electrical inspector. How do I go about checking if this will work or not? (I'm not familiar with series rating).
I'm currently working on a small retail shop and experiencing a problem. The main switchboard (existing) has an AIC rating of 57 KAIC. Using this figure, I arrived at 39KAIC at my 100A, 277/480V panel. Using the calcs., I spec'd the panel with an AIC rating of 42 KAIC. Now, our specifications allowed the panels to be series rated. I recently found out that the contractor has installed a 14 KAIC rated panel. At first glance, I don't believe this will work (not only that, it's not conforming to my design). Unless I can come up with supporting documentation, I believe the project will get red tagged by the electrical inspector. How do I go about checking if this will work or not? (I'm not familiar with series rating).