110.21(C) requires the following:
what is the "rated" value? Is this the value that is less than the actual available fault current, that i can use because of the series rating (i.e 10k for a 10k downstream breaker that series rates with an upstream 65K)? OR is this the actual fault current value? I always assumed this was the lesser series rating value, but I just got an inspection and the inspector is saying this should be the actual fault current available at the downstream equipment.
Tested Series Combination Systems. Equipment enclosures
for circuit breakers or fuses applied in compliance
with the series combination ratings marked on the equipment
by the manufacturer in accordance with 240.86(B)
shall be legibly marked in the field to indicate the equipment
has been applied with a series combination rating.
The marking shall meet the requirements in 110.21(B) and
shall be readily visible and state the following:
CAUTION — SERIES COMBINATION SYSTEM
RATED ____ AMPERES. IDENTIFIED REPLACEMENT
COMPONENTS REQUIRED
what is the "rated" value? Is this the value that is less than the actual available fault current, that i can use because of the series rating (i.e 10k for a 10k downstream breaker that series rates with an upstream 65K)? OR is this the actual fault current value? I always assumed this was the lesser series rating value, but I just got an inspection and the inspector is saying this should be the actual fault current available at the downstream equipment.