A customer has too much available fault current into his Industrial Control enclosure. I believe he has 65K. The main means of disconnect within his controller is a GE Spectra breaker, rated at 42K. Can he use series rating (combination of fuse and GE breaker) to reduce his availavle fault current?
Asked a different way, I know series rating calls out for both devices to "go" at the same time, but this would be a UL listed combination. So.....can we use the current limiting ability of the fuse to protect the breaker?
We have some motors and contribution is not a factor at this time...
Dave
Asked a different way, I know series rating calls out for both devices to "go" at the same time, but this would be a UL listed combination. So.....can we use the current limiting ability of the fuse to protect the breaker?
We have some motors and contribution is not a factor at this time...